Hi all, Thank you for your effort. I am in a similar situation because I have at home a Wolf heatpump (CHC/CHA) with Solar module SM-1 and control module BM-2. As you can see in #776 I am encountering difficulties getting the data (also getting devices to properly show up). I checked out your files in the 22.4.x/de folder and I am currently using them, just restarted ebusd. Please count me in if you need any further information, as I can debug and give data from the system. Mainly because I want this to work :D |
|
My System Layout as Example and a small update on whats going on I have a CGB-35 with BM integrated and directly controlling the hot water tank I scanned my bus and sorted the devices by id and function. I see this communication on regular basis:
Most communication uses the speced protocol messages. |
|
Hello! Currently i cannot get the .csv stuff to work Is this as it looks at your setup: 1 directory, 5 files Greetings |
|
@ulda you are correct, that there is no publicly available documentation from Wolf regarding their messages on the ebus, but they published a desktop application in the past and are still publishing an android app which contains metadata files with all information needed to map ebus addresses to readable names and even find out which are supported by a concrete setup. I've "looked closely" at the Wolf Smartset application (and written an ISM to MQTT Adapter). I've already linked the information in #460 (comment) and hoped it would spread further within this community. This tool is not directly talking to the bus, but to an ISM module from Wolf, which basically translates XML to ebus. In the meantime i also extracted, packaged and used the official binaries in a tool to automatically extract all parameters from a given setup without the requirement to run the Wolf app just by connecting to the ISM. So from a user perspective (with the required hardware) it's just:
and you have read and write access to all parameters I haven't thought this through, but I'm pretty confident that it should be possible to write some kind of adaptation layer which translates the protocol from the official app to ebusd or some kind of adapter and thus be able to use the app to extract the exact configuration needed for ebusd. So it should be possible to get the same experience of "run this binary to generate a complete config" for users with an ebus adapter/without an ISM. |
|
Hi, is this topic still relevant? I actually only want to read out 3 values, pump on or off, temperature in the solar buffer and the modules on the roof. Thanks this is how it looks at the moment: root@vclin:~# cat /var/log/ebusd.log |
|
#950 helped a lot. At least I have some basic fields working now, working on getting more to work. |
|
Hi there, i'll probably tackle what @zivillian talked about in the near future about generating the config files from the xml files. So it would probably go like: Few things:
I havent used ebusd a lot but from what i can see around forums and in ebusd wolf has two "special" messages:
I now provide a more reasonable way to inspect the xml files, a json file compiled from the xml files in case anyone wants to take a look at them if they are missing definitions. LIST OF WOLF DEVICES THE APP RECOGNIZES: My device is a COB this means that i can search for that in the json: {
"DTID": "90000",
"name": "COB",
"parameters": [Then inside the parameters array you can find the parameter you want to read/write by their name, for example "Boiler water temperature": {
"type": "NumericParameterDescriptor",
"PTID": "90001",
"name": {
"DEU": "Kesseltemperatur",
"ESP": "Temperatura caldera",
"GBR": "Boiler water temperature"
},
"RemoveConditionId": "False",
"ReadOnlyConditionId": "True",
"InactiveConditionId": "False",
"IsSnapshotTransmitEnabled": "false",
"Decimals": "1",
"ControlType": "NumericInput",
"converter": {
"type": "NumericConverter16Template",
"TelegramNr": "13",
"Type": "SS10"
},
"read_command": "CC0D00"
}Again i have no clue what half of the things mean and its even missing many others that i didnt believe to be relevant, but they seem pretty self explanatory. ReadOnlyConditionId probably means that the parameter is read only. Then "converter" is the important part, it tells you how to read/write the value, in this case our dear neighbor zivillian already did the hard part in https://github.com/zivillian/ism7mqtt So we know that TelegramNr is what you need to send transformed the following way (Python for convenience): def telegram_to_read_command(telegram_num):
# Convert to hex, little endian, prefix with CC
hex_str = f"{int(telegram_num):04x}"
little_endian = hex_str[2:] + hex_str[:2]
return "CC" + little_endian.upper()So 17 -> Gives us 0x0D00 -> CC0D00 According to #167 the CC part is irrelevant since its a CRC that wolf devices ignore so the TypeSpec template defaults it to 00 Then when you get the ebus response you need to convert it based on the "Type", again zivillian did the hard part, the options are: case "US":
result = JsonValue.Create(_value.Value);
break;
case "SS":
result = JsonValue.Create((short)_value.Value);
break;
case "SS10":
result = JsonValue.Create(((short)_value.Value) / 10.0);
break;
case "US10":
result = JsonValue.Create(_value.Value / 10.0);
break;
case "SS100":
result = JsonValue.Create(((short)_value.Value) / 100.0);
break;
case "SSPR":
result = JsonValue.Create(((short) _value.Value) * (1.0 / 255));
break;
case "US4":
result = JsonValue.Create(_value.Value / 4.0);
break;
case "IntDiv60":
result = JsonValue.Create(_value.Value / 60.0);
break;I havent looked what the equivalent is in ebusd for all of them but SS10 is temp10 in the TypeSpec. Full TypeSpec example that worked for my boiler: import "@ebusd/ebus-typespec";
import "./_templates.tsp";
import "../opdata_inc.tsp";
using Ebus;
using Ebus.Num;
using Ebus.Dtm;
using Ebus.Str;
namespace Wolf;
// 0x35 is my boiler, pure guess tho, i know its this one because of the few messages i can see in the bus
@zz(0x35) //
namespace hc {
/** Boiler temperature */
@id(0x0D, 0x00) // Message 0D00
@poll(2)
model BoilerTemp is ReadonlyRegister<temp10>;
/** Accumulator temperature */
@id(0x0E, 0x00) // Same reasoning as above but with TelegramNr 14 thus 0E00
@poll(2)
model AcumulatorTemp is ReadonlyRegister<temp10>;
}This "compiled" to this csv: type,circuit,level,name,comment,qq,zz,pbsb,id,*name,part,type,divisor/values,unit,comment
*r,
r2,Hc,,BoilerTemp,Boiler temperature,,,5022,000d00,value,,UIN,10,°C,temperature
r2,Hc,,AcumulatorTemp,Acumulator temperature,,,5022,000e00,value,,UIN,10,°C,temperatureI havent tried writing yet, but the json contains all possible values for write parameters: {
"type": "ListParameterDescriptor",
"PTID": "410010",
"name": {
"DEU": "Programmwahl",
"ESP": "Selección de programa",
"GBR": "Prog. select."
},
"RemoveConditionId": "False",
"ReadOnlyConditionId": "False",
"InactiveConditionId": "False",
"IsSnapshotTransmitEnabled": "true",
"MinValueCondition": "0",
"MaxValueCondition": "3",
"ControlType": "ProgramSelectionListView",
"KeyValueList": [
{
"key": "0",
"value": {
"DEU": "Standby",
"ESP": "Standby",
"GBR": "Standby"
}
},
{
"key": "1",
"value": {
"DEU": "Auto",
"ESP": "Auto",
"GBR": "Auto"
}
},
{
"key": "2",
"value": {
"DEU": "Sommer",
"ESP": "Verano",
"GBR": "Summer"
}
}
],
"converter": {
"type": "NumericConverter16Template",
"TelegramNr": "10100",
"Type": "US"
},
"read_command": "CC7427"
}If anyone knows how ISM7 identifies the devices it would be of great help. If its not possible i will just probably create the TypeSpec without |
|
Hi everyone, great thread! I have a working Wolf CGW2 config, able to read quite a lot of data using the following csv: I only see 1 broadcast message on the bus, but can read values using polling and also via the force read in the command line. I have a wiring question though. I have my AM module integrated into the boiler (snapped in place into the unit) and have my ebus adapter wired to the ebus connection on the PCB. Is this the right way to do it? Or should my ebus adapter be wired "between" the boiler and the AM module? I was not able to write anything to the boiler (wanted to set DHW target), I get an error: Anyone got writing of settings working? |
|
Hi all, |
|
Hi guys, I answer here, as I plugged yesterday my Solar Module SM2 (with BM2 screen) via eBus (device EBUS to WiFi Adapter Module V6.3) to my home assistant server running MQTT and ebusd. At first, I struggle to get it recognized, and finally I have the values I am looking for: (collector temp, solar tank exchanger temp, solar return line temp, pump state, and even pump hour meter). My install SM2/BM2 old genAlthough this is a new installation, I installed an old SM2 gen1 device I recovered. Firmware is old (228-02 on old SM2 motherboard). First of all, when configuring ebusd, I had to ignore enhanced mode (can't connect to bus), and switch to regular mode. In ebusd configuration, line "Network adapter address', I get rid of enh (enh:IP:port) and use IP:port instead (ie: 192.168.1.34:3333) with specific 3333 port (regular mode, read/write). At this stage, device was talking to ebusd and gives me warning about Kromschroeder device ID 76 not recognized. I found quickly that it is the same brand as Wolf, and a direct symbolic link exist in CSV conf. Working CSV FileAfter some struggling, I wrote this CSV file. Upload that file to your home assistant server in Values does not appears in MQTT device (solved)I was annoyed with values not showing in MQTT device, but available in MQTT data (using MQTT explorer). Other valuesI tried map other values, like yield day, yield total, but it does not work (returning 0). Hope this helps! |
|
I've been running a Wolf CGG-2-18 with BM control module on ebusd for a while now and finally got around to publishing the configuration. Full stack including MQTT auto-discovery for Home Assistant: A lean version (CSV only) was also merged into puni2k's collection: Happy to answer questions. |
|
One more finding: the Wolf BM has no battery-backed RTC and loses its time and date Documented with shell command and HA automation notes here: |
|
Some findings from a Wolf CGU-2-10 + old BM (ebusd 26.1 HA add-on, adapter v5), in case they help others: 1. Output A1 (circulation pump) is readable at the boiler 2. BM DHW setpoint and operating mode – read AND write at slave Mode values verified at the BM: 1 = off, 2 = timer, 3 = sun+DHW, 4 = moon+DHW, 5 = DHW only. Changes show up on the BM display immediately. 3. Heating vs. DHW demand from broadcast Thanks to @dktzde for the CRC8 finding and to @realResi – both saved a lot of guessing. _homa |
Wolf boilers on ebusd: the checksum is solved — read and write every registerTL;DR — The mystery byte in a Wolf read telegram is a CRC8 with polynomial Tested on a Wolf FGB-K-28 (ebusd 25.1, eBUS shield, ioBroker). 22 of 22 generated IDs are 1. Why this has been hardWolf publishes no eBUS documentation. Every Wolf config in the wild is hand-made, partial, and Reads are The last two bytes are obviously the TelegramNr little-endian. The first byte is the problem. 2. The checksumIt is linear over GF(2), which is what makes it recoverable. Take known-good (byte, TelegramNr) function wolfCrc(telegramNr) {
let c = telegramNr & 0xff;
for (let i = 0; i < 8; i++)
c = (c & 0x80) ? (((c << 1) & 0xff) ^ 0x5c) : ((c << 1) & 0xff);
return (c ^ (telegramNr >> 8)) & 0xff;
}
const hx = n => n.toString(16).padStart(2, '0');
const readId = tn => hx(wolfCrc(tn)) + hx(tn & 0xff) + hx((tn >> 8) & 0xff);A CRC8 chain with polynomial Checks that matter:
Bonus: running this over an existing config is a good way to find typos. It flagged one in 3. Writes — and why yours probably do nothingWrites use a different address and a different ID format:
Two things people get wrong:
Proof, on a deliberately harmless register ( And the one that matters — the DHW setpoint, TelegramNr 19, write ID Test writes on something harmless first. 4. Getting the register list for your Wolf deviceYou do not have to guess which TelegramNrs exist. Wolf's own SmartSet/ISM7 metadata is public
Which one are you? Look at your ebusd scan string. Mine says Type mapping: 5. Things that cost me hours
Validate a config offline, as a normal user, before installing it: Copy your config tree somewhere writable, edit, check. It prints Do not force-read many registers back to back. I ran 32 sequential Adding a write row whose name matches an existing read row does NOT increase Polling more costs nothing. I went from 28 to 60 polled messages and the bus symbol rate Values reading 6. ioBroker integrationMQTT. ebusd's own MQTT integration publishes reads fine: Note it ships exec('ebusctl write -c heating dhw_target_set 50', () => {
exec('ebusctl read -m 0 -c heating dhw_target_set', (e, out) => log('now ' + out));
});Always read back and verify. A write that silently does nothing is the failure mode here. Poll priority gotcha. If you use the Home Assistant MQTT profile, Two scripts are attached:
Useful enum decodings (from Wolf's own 7. SafetyThis is a gas appliance. A few things I would not do:
8. What it got meA Wolf FGB-K-28 that exposed 28 registers, six of them permanently dead, now exposes 60 — at Anlagendruck (system pressure, bar) · Abgastemperatur (flue gas) · Modulationsgrad · Plus working writes, which turned into an automated weekly DHW disinfection cycle and a Three errors found in a config that had been running for years: a wrong checksum on Files
CreditThe parameter database is zivillian/ism7mqtt's extraction Corrections welcome, especially from anyone who can confirm or refute the checksum on a non-FGB |


Uh oh!
There was an error while loading. Please reload this page.
Hi everybody
I started this discussion to collect everything we have about WOLF Heiztechnik hardware.
and this nearly nothing at the moment (2022-12-29). At least I did not find much googling.
The WOLF systems sometimes also announce manufacturer KROMSCHROEDER. Hold these as synonome.
I did not find any documentation of manufacutrers side of the bus - they keep every docu closed behind ther support portal.
But in the ebus spec there are some defaults documented, and over on ebus-wiki.org they collected the spec documents.
Some of the 05xx and 07xx and 08xx messages can be decoded using this documentation.
But until now nobody used this to create some default CSVs to use for unknown systems.
They also startet to collect about the vendor specific command set 50xx but they did not come far and what I found in the 2.x.x part of this repository look better.
It looks to me like someone poked on the user terminal for each setting and then looked at the messages it generates on the bus.
This would be another way to come forward with reverse-engineering the 50xx command set at least to get some data out of it.
The configs of the 2.x.x directory of this repo did not work for me, either.
Some messages had errors on my CGB-35/KK/BM system. And it was a hazzle to get mqtt autoconfiguration running.
becaus the old names do not fit with the default mqtt-hassio.cfg filtering sheme.
So I startet a fork of the ebusd-configuration repo here at github to put in what I have now: some small set of entities generated from the ebus of my CGB-35 gas heating system.
Now I want you to join to create some working default configuration from this devices.
You can help out
We all would be happy if you post your findings here.