True, There is no TOP with read SG status. |
|
Bytes 71-74 just store the values , with are presset in HP (procentages) , not gives status.... |
|
Ok got it , byte no 124: |
|
To be honest , you will do it better with your external automation.... But anyway this feature could be implemented anyway ( if there is somone for test :) ) |
|
Hi, today I tried also the same but made no progress.
Am I missing something? |
|
There is no reason to use the SG ready. You can easily change all temperature requests yourself already (using heishamon commands) so why use SG ready for this? |




Uh oh!
There was an error while loading. Please reload this page.
Uh oh!
There was an error while loading. Please reload this page.
I have the optional CZ-NS5P board in my K series, switching from cooling to heating and vise versa works perfect (I do this with a relay from my DigitalStrom smart home system). Also the heatpump seems to react to the off signal based in the following bit1 and bit2 settings:
bit1 Open bit2 Open -> normal working mode
bit1 Short bit2 Open -> both Heatpump and DHW off
When switching off nothing is shown in the heishamon monitor (or I don't know where to look) but the external pump switches off.
Now I need the other bit1 and bit2 setting to activate capacity mode 1 and 2 which settings I made in the installer menu.
bit1 open bit2 short -> capacity 1
bit1 short bit2 short -> capacity 2
But the big question is how can I see if the heatpump works like requested, I see no values in the heishamon monitor changing ?